douglasgdmw wrote:Thanks but unfortunately we really need 35kw. Looks like we have been recommended a Grant Vortex ECO 26/35.
However trying to also determine whether its best yo go for a Grant Vortex Pro (VTXOM26/36 or VTXOM36/46) or a Grant VortexBlue (VTXBFOM36).
The installer who quoted did say the Worcester ones were rubbish and would not recommend them for oil boilers.
Far be it for me to argue your needs, but are you sure about that or is it just what you have been told?
35Kw is a F**K big boiler in real terms, (not talking about combi's here), look at it like this, typical radiator is between 1 and 4 Kw (4Kw rad is going to be a double at least 4.5M long!)
Add up the total rads, and size boiler accordingly, remember though that usually a rad will be higher output than the room actually needs, so even if the rad count says X Kw, in reality, (assuming TRV's etc) you don't need a boiler that is >= X Kw.
My last place had 17 rads, total 35Kw by rad, and I used a 28Kw boiler, it was never stretched, spent most of it's time throttling down to ~12-13Kw, the only time it ever ran at 28Kw was the first 10 mins from stone cold.